What about High And Low Pressure steam boilers? Is it equally good to be installed at ? If where it is installed over Inlet feed ? or some else place. Pl. respond.

Published by

What about High And Low Pressure steam boilers? Is it equally good to be installed at ? If where it is installed over Inlet feed ? or some else place. Pl. respond.

1 Comment

We have units fitted on steam boilers all over the world.   You are correct the units are fitted on the cold/cooler inlet feed.  The reasoning for this is that you condition the water prior to heating it.  The heating of the water is what causes the scale to drop out of suspension.  The Hydroflow unit causes clusters of ions Ca+ CO3- in the flow and these then form CaCO3 crystals when the water is heated. The crystals tend to be quite spherical and do not adhere to surfaces well so any that aren't washed through can easily be cleaned out rather than having to use strong chemicals or physical attack!

I hope that helps.