I agree with Vinod below. ...

Published by

I agree with Vinod below. Assuming the problem is scaling rather than biofouling, the membranes at the brine end are most likely to be scaled. If you can replace just the last one there should be a disproportionate improvement but moving them won't achieve much.

A long shot, but MAYBE if you rotate the membranes and then do a scaling CIP it may be more effective.

Have you tried a high pH CIP to treat biofouling?

Finally, does your system allow osmotic backflow on shut down? That helps a lot to remove fouling.

1 Comment

thanks for your information.
shall i identify the most scaled / fouled membrane by measuring the weight of individual membrane?
i have tried high pH cleaning, but no significant improvement.
since it is small plant (9 m3/hr), we don't have osmotic backflow arrangement in our plant. could you please let me know will the osmotic backflow reduce the chance of fouling and scaling? how dose it works?

Published by

Permalink

1 Comment

Maybe best if you can send a membrane unit off for analysis to a specialist to see what went wrong. I've never heard of weighing the membranes to determine which is the most fouled but maybe it can be done. Perhaps not very helpful advice now but maybe worth always having a spare sealed membrane unit in store so you can try changing out different existing units.

Osmotic backflow, which a well designed plant should allow but many do not, happens on each shutdown. Flow back THROUGH the membrane helps to clean it, instead of a CIP which washes OVER the feed surface.

I can recommend an Australian consultant to provide advice but I guess you are in Mumbai and that is problematic.